    Couple of quick thoughts - those two breakers that share a neutral should always have been next to each other; not across from and not separated from. Second thought - any 30 amp breaker requires # 10 copper wire. I'm guessing the wire already there is only #12 if protected by a 20 amp breaker. If so, even if they built a 30 amp arc fault breaker it'd be a no go. I realize wiring already in the walls is a limiting factor but there's a good reason why the National Electric Code stopped allowing shared neutrals around 20 years or so ago.

    0
  • Mr. Perfect
    firstharmonic: 31515141069211/comments/31515149250715

    Couple of quick thoughts - those two breakers that share a neutral should always have been next to each other; not across from and not separated from. Second thought - any 30 amp breaker requires # 10 copper wire. I'm guessing the wire already there is only #12 if protected by a 20 amp breaker. If so, even if they built a 30 amp arc fault breaker it'd be a no go. I realize wiring already in the walls is a limiting factor but there's a good reason why the National Electric Code stopped allowing shared neutrals around 20 years or so ago.

    Thanks. I had thought so too... that they should have been next to each other. And yes, the wire is #12, so that should have been my first clue that I can't do a 30A.

    0
  • Mr. Perfect

    Note that the range hood has always been on the micro circuit, I just tied in two outlets and lights because it was the best available circuit for it based on location. If I have to move those, it's going to be a huge pita.

    0
  • jimdeere

    ^^^^^^This.

    plus

    Give the microwave it’s own circuit.

    Air fryers, toaster ovens, insta pots, etc. are all high wattage. This ain’t your grandma’s kitchen.

    3
  • Mr. Perfect

    Well, it just passed inspection with the handle tie.